Kevin Zippel <zippelk at yahoo.com> wrote:
>... I have a ~2500sf farmhouse in zone 5b, Finger Lakes region New York.
>Our house has average insulation, except the attic which we just bumped up
>to R70. The house had ducted air heating via a propane furnace, which we
>promptly shut off and went with woodstove heat. The house is in a
>floodplain and there is a free-flowing artesian well on the side of the
>house. Without a pump, the water comes out at 5 gal in ~6.5min, or ~3/4
>gpm, or ~45 gph. Would it be possible/reasonable to run that through a
>water-to-air heat pump (likely with supplemental pumping from the well) and
>run the air directly into my existing ductwork?
Cooling 375 pounds per hour of 45 F water to 35 would be 3750 Btu/h, but how
about solar heating with a COP of 1000 or more, vs 3 for a heat pump?
Binghamton gets 610 Btu/h-ft^2 on a south wall on an average 26.5 F December
day, more than Rochester, with 560, where I designed a system to solar heat
a 1200 ft^2 addition with R30 walls with a 240 ft^2 twinwall polycarbonate
sunspace wall and 144 ft^2 of single air heater glazing inside that with 64
ft of fin-tube pipe near the top to heat a 1000 gallon STSS tank in the
basement, in a kind of thermal cogeneration. If all goes well, on an average
day, warm sunspace air will heat 2400 pounds of water in 4" PVC pipes under
a foil-covered cathedral ceiling, and a slow ceiling fan and a room temp
thermostat and an occupancy sensor will keep the room 70 F. The water will
cool to about 60 F by dawn, with a 50 F night setback. On a cloudy day, we
will pump some tank water up through the ceiling pipes, and the tank will
also heat DHW with a pressurized copper coil. My TMY2 simulation shows 100%
solar space heating in an average year, with a min tank temp of 91 F in
mid-December.