    When you draw water from a tank water heater you draw cold water in 
from the well or municipal supply, this is cold water, 45-65*F. When the 
temperature of the tank goes down about 20*F from the set point, the 
burner turns on and heats the tank back up. Bringing a return line from 
a heating loop with a higher return temperature is no different, how 
would it be any more of a problem?
    With radiant floors you want no more than a 87*F surface 
temperature, a slab will require the lowest water temperature 
(110*F+/-), and will rise as you use add carpet, or go to wood floor 
systems, and the water temperature required will increase upwards to 
(170*F+/-).
    One benefit of a combined system that may not have occurred to you, 
is that since your heat loads are lower than the output of the boilers, 
the combined system will mitigate this since the volume of water acts as 
a buffer. In fact if you add a small storage tank to a boiler loop this 
will let the boiler run longer with your small loads (won't short cycle 
which is less efficient). I am also struggling with this issue also, and 
most gas furnaces are oversize too, when your loads are 15-20KBtu/hr.
    What kind of tank do you like with internal heat exchangers? Heat 
Transfer Product is coming out with some tanks with a heat exchanger on 
the bottom for solar, and on one top for a boiler loop (I have been 
working on such a design the past year).
    Takagi and Rania hold there efficiency the best just heating cold 
water (from Skip Hayden, a great Canadian), I would love to have a link 
to research on solar backup, since many people push tankless for this 
application, and am considering it for my own system, although I would 
like to have it in a closed loop to reduce mineral deposits and reduce 
maintenance, and protect the expensive investment. I actually want to 
use a high efficiency (90%+) condensing boiler for backup.


Shawna Henderson wrote:

>I think the health issue is not so easily shaken off. THe line feeding 
>the water heater in a non-radiant floor house comes directly from the 
>well or municipal line, at ±45*F. This is not salmonella-breeding 
>condition in the line, nor in the water heater. Also, there is no 
>recirculation from the end use back into the tank (ew, the thought of it!).
>
>When the return from the floor comes into the tank, it is coming in at a 
>lower temperature than the floor required. Say the floor requires 85*F. 
>The return will be somewhere between 70 and 80*F. This dumps into the 
>DHW tank when there is potentially no other demand on the tank. Anything 
>under 120*F as a constant temperature is cause for concern in the tank. 
>I simply don't see how anyone can guarantee that this condition won't 
>ever occur. The careful planning of your second system is also not 
>guaranteed, especially in a D-I-Y situation, where one cannot make any 
>assumptions about the knowledge/skill level of the installer.
>
>I can't bring myself to recommend the shared tank to anyone because I 
>can't see the overall benefit -- the cost of careful planning and extra 
>valves and such outweighs the cost of going to a different configuration 
>all together, one that doesn't carry any risk of contamination of 
>potable water. I usually spec an integrated heat exchanger in a storage 
>tank or a small boiler system However most houses I design have such a 
>small load that the boilers are embarassingly oversized. That's why I 
>got 'hooked' on the integrated HX w/storage tank (which also lends 
>itself very well to a now-or-future solar thermal installation).
>
>Here's another bit of info from Natural Resources Canada re: Tankless 
>waterheaters. Performance goes down dramatically when coupled w/tempered 
>water from a solar thermal system or other upstream preheating source. 
>THis is because the units are built to work most efficiently when there 
>is a large temperature difference. Also, I have experienced challenges 
>with propane-fired units w/piezo-electric ignition (Bosch specifically), 
>where wellpump & expansion tank did not give adequate pressure to push 
>the p-e ignition. THis resulted in no hot water except when faucets were 
>cranked wide open. Problem mitigated *but not solved* by putting in 
>larger expansion tank. Municipal feed at constant pressure, no problemo.
>
>s.
>
>Lawrence Lile wrote:
>
>  
>
>>We discuss the potential of radiant floors to breed bad bugs
>>occasionally here.  There are two schools of thought, both equally
>>valid:
>>
>>1.  Isolate the radfiant floor from the domestic water supply. 
>>
>>2. Integrate the radiant floor into the domestic supply, in a way that
>>there are no dead spots, the entire radiant floor system is refreshed
>>with cold water whenever the water heater demands water.  This is
>>accomplished with a system of one-way valves.  Think of it this way:
>>Does anyone worry about salmonella growing in the line feeding your
>>water heater in a standard non-radiant floor house?  No.  If that line
>>was ten feet long would you worry?  No.  How about 50 feet, or 100 feet?
>>No.  The radiant floor, in a non-heating season, becomes a 100 foot line
>>feeding your hot water heater.  The Radiant Company has some good
>>diagrams as to how this works.  
>>
>>Either system can work safely, the second system needs to have some
>>careful planning to avoid dead spots that never get flushed out.  
>>
>>I would recommend you dump your tank type water heater in any case, and
>>go with a tankless.  You'll spend several thousand on this whole system
>>by the time you are done, if you install a tankless you'll get a higher
>>efficiency water heater, and never run out of hot water.  It is likely
>>that your tank type is ready for it's ten year replacement schedule
>>anyway, just retire it early.  
>>
>>
>>Lawrence Lile
>>
>>
>>-----Original Message-----
>>From: greenbuilding-bounces at listserv.repp.org
>>[mailto:greenbuilding-bounces at listserv.repp.org] On Behalf Of Shawna
>>Henderson
>>Sent: Tuesday, September 26, 2006 9:20 AM
>>To: rigaziodesigns
>>Cc: Greenbuilder list
>>Subject: [BULK] Re: [Greenbuilding] suspended slab
>>Importance: Low
>>
>>Most definitely you want to isolate the DHW from the floor. The two
>>systems should never be fed from the same tank. The reasons are twofold:
>>
>>1. If you run the floor off the DHW tank without a step-down or mixing
>>valve, you are going to be running the floor too hot, and you will end
>>up with extremely high bills. Also, the tank has a longer recovery time
>>than a boiler, so you will potentlally suffer cool showers if there is
>>too much demand on the tank at one time (think cold winter morning, high
>>heatling load).
>>
>>2. And more important than #1 -- the cooler water running through the
>>floor and back into your DHW tank can drop the temperature of the water
>>to a point where salmonella and other greeblies can flourish. Then your
>>whole family's sick and you might not have enough hot water to clean up
>>after them...
>>
>>There are DHW tanks out there that have an integral heat exchanger in
>>them, allowing you to store hot water iin the tank for DHW, but run the
>>floor (with its lower temperature demand) through the heat exchanger. No
>>cross-contamination. Loverly. Only one heat exchanger. Works divinely
>>with a direct-vent propane unit tied to a solar thermal system and a
>>second tank in parallel.
>>
>>Also, with the slab, definitely insulate under it. And don't be swayed
>>by bubble pack insulation, 'radiant' or not. There's a Canadian
>>manufacturer (truefoam) that puts out a product that is specifically
>>made for hydronic floors. It's a 1" or so rigid foam that has grooves
>>cut into it at 6" centres, so you just fit the PEX into it. I wouldn't
>>recommend it for new slab construction, but for a retrofit situation,
>>its great. The reason I wouldn't recommend it for new constr. is that it
>>puts the heating tubes in the lower 1/3 of a 3"or better slab, reducing
>>the efficiency of the heat delivered and also increasing the lag time. 
>>With a retrofit 1.5" overpour (or suspended slab, a term that's new to
>>me), this is not so much of an issue.
>>
>>Hope this helps
>>
>>Shawna H.
>>
>>rigaziodesigns wrote:
>>
>>    
>>
>>>George,
>>>
>>>When you say "The big question is do you need to isolate the radiant 
>>>floor from the domestic hot water, with a heat exchanger and 2 pumps." 
>>>do you mean he may be required by code or is this a functionality
>>>
>>>      
>>>
>>question?
>>
>>    
>>
>>>Thanks all!
>>>Lisa
>>>
>>>On 9/25/06, George J. Nesbitt <geoedb at idiom.com> wrote:
>>>
>>>      
>>>
>>>> Uninsulated slabs can be a real comfort problem. A well designed 
>>>>forced air heating system can overcome this, although not as easily as
>>>>
>>>>        
>>>>
>>>>heating the floor directly.
>>>> Ideally you would add insulation on top of the existing slab and 
>>>>then install the radiant floor. If you don't you will get more heat 
>>>>loss through the slab. If you use the existing water heater it needs 
>>>>to have enough capacity to heat both the domestic hot water and the 
>>>>floor. The Gas Research Institute has guidelines on sizing the water 
>>>>heater, I don't know if it is available on the Internet. You can 
>>>>possibly turn of the radiant floor when there is domestic hot water 
>>>>draw to prevent running out of hot water sooner. The big question is 
>>>>do you need to isolate the radiant floor from the domestic hot water, 
>>>>with a heat exchanger and 2 pumps. Taco makes an integrated exchanger
>>>>
>>>>        
>>>>
>>and pump system.
>>
>>    
>>
>>>> Don't forget that you have to cut down any doors within the area 
>>>>being raised.
>>>>
>>>>
>>>>rigaziodesigns wrote:
>>>>
>>>>        
>>>>
>>>>>A friend of mine recently moved into an existing house with slab on 
>>>>>grade floors in the main living space... and of course the floors are
>>>>>
>>>>>          
>>>>>
>>>>>cold. He looked at the Radiant Floor website (see below) and thinks 
>>>>>the suspended slab installation is for him since if he uses the new 
>>>>>concrete as his finished floor he will only loose 1 1/2" head room. 
>>>>>He also assumes that
>>>>>
>>>>>          
>>>>>
>>>>he
>>>>
>>>>        
>>>>
>>>>>will be able to heat the space off of his domestic hot water heater. 
>>>>>BTW,
>>>>>
>>>>>          
>>>>>
>>>>He
>>>>
>>>>        
>>>>
>>>>>lives in the washington DC area. Does anyone have experience with 
>>>>>this
>>>>>
>>>>>          
>>>>>
>>>>type
>>>>
>>>>        
>>>>
>>>>>of system or know if they work well and are worth the investment?
>>>>>
>>>>>http://www.radiantcompany.com/details/suspendednotes.shtml
>>>>>
>>>>>Thanks,
>>>>>Lisa
>>>>>_______________________________________________
>>>>>Greenbuilding email list
>>>>>List info:
>>>>>
>>>>>          
>>>>>
>>>>http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.
>>>>org
>>>>
>>>>        
>>>>
>>>>>List email: Greenbuilding at listserv.repp.org Managed by BuildingGreen,
>>>>>
>>>>>          
>>>>>
>>>>>Inc. http://www.buildinggreen.com
>>>>>   publisher of Environmental Building News and GreenSpec(r) Hosted
>>>>>
>>>>>          
>>>>>
>>>>>and archived by REPP / CREST http://www.crest.org
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>          
>>>>>
>>>>_______________________________________________
>>>>Greenbuilding email list
>>>>List info:
>>>>http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.
>>>>org List email: Greenbuilding at listserv.repp.org Managed by 
>>>>BuildingGreen, Inc. http://www.buildinggreen.com
>>>>   publisher of Environmental Building News and GreenSpec(r) Hosted 
>>>>and archived by REPP / CREST http://www.crest.org
>>>>
>>>>
>>>>        
>>>>
>>>_______________________________________________
>>>Greenbuilding email list
>>>List info: 
>>>http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.o
>>>rg List email: Greenbuilding at listserv.repp.org Managed by 
>>>BuildingGreen, Inc. http://www.buildinggreen.com
>>>    publisher of Environmental Building News and GreenSpec(r) Hosted 
>>>and archived by REPP / CREST http://www.crest.org
>>>
>>>      
>>>
>>_______________________________________________
>>Greenbuilding email list
>>List info:
>>http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.or
>>g
>>List email: Greenbuilding at listserv.repp.org Managed by BuildingGreen,
>>Inc. http://www.buildinggreen.com
>>     publisher of Environmental Building News and GreenSpec(r) Hosted
>>and archived by REPP / CREST http://www.crest.org
>>
>>_______________________________________________
>>Greenbuilding email list
>>List info: http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.org
>>List email: Greenbuilding at listserv.repp.org
>>Managed by BuildingGreen, Inc. http://www.buildinggreen.com
>>     publisher of Environmental Building News and GreenSpec(r)
>>Hosted and archived by REPP / CREST http://www.crest.org
>>
>>    
>>
>
>
>_______________________________________________
>Greenbuilding email list
>List info: http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.org
>List email: Greenbuilding at listserv.repp.org
>Managed by BuildingGreen, Inc. http://www.buildinggreen.com
>      publisher of Environmental Building News and GreenSpec(r)
>Hosted and archived by REPP / CREST http://www.crest.org
>
>
>  
>


More information about the Greenbuilding mailing list