Sacie writes:
>... I have the ability to bring in cold outside air (not HRV) via a
>minimally ducted system... Designed as an experimental system for a
>tight house, the machine's primary use is to dehumidify basement
>storage in the summer.
I wonder how it would do that. With a clever control, you might move
outdoor air through the basement when it contains less moisture, in the
absolute sense. A less weather-dependent passive system might have
desiccant clay bags hanging on wires in a glazed box connected to the
basement with an air-air heat exchanger. The sun would heat the bags to
evaporate water, and the heat exchanger would make the basement and box
air about the same temp, so heavier drier air would flow down into the
basement via gravity. Uline sells nice Tyvek clay bags for about $1/lb.
They can hold 28% of their weight in water.
> I run small humidifiers in the above very dry room but am wondering if
> I run the cold air in, if I might be more successful in raising the
> humidity?
More likely you'd lower humidity in wintertime. To raise it, you might
airseal the house more, with a blower door test.
>... This morning is typical. High teens outside, RH in the 40s inside,
>with temps in the mid to high 60s and a nice bead of water across the
>base of every window in the house, including those that are inoperable.
>Simple difference between indoor and outdoor temps?
No. The indoor RH matters too. Condensation happens when the indoor
window surface temp is less than the dew point of indoor air. If you put
a few ice cubes in some room temp water in a glass and stir it with a
thermometer until you see condensation, you can read the dew point on
the thermometer. Or calculate it: with room temp T (F) and RH R (%), Td
= (460+T)/(1-(460+T)ln(R/100)/9621)-460, where ln is the natural log on
your $10 Casio fx-260 calculator. For example,
T = 70 F and RH = 50% make Td = 520/(1-530ln(0.5)/9621)-460 = 50.5 F.
Better windows with lower U-values have higher indoor glass temps, with
less chance of condensation.
>Second question: if there are no vents below or above (an open,
>therefore multi-story house with no ability to close either up or down)
>and a small exhaust (don't know how many cfm pulled) in the main center
>floor, what is the effect? House tight, but many many windows.
With a few air leaks, running the fan would likely introduce fresh air
and lower the indoor RH in wintertime.