On Mar 08, 2007, at 14:16, Lawrence Lile wrote:
> I am considering hacking a dryer so that it has an outside air
> combustion intake, so that at least it doesn't suck up expensive heated
> indoor air to blow outside. That would involve adding a second hole in
> the back of the unit, plugging up any vent holes, and running the sair
> intake pipe outside through a screen.
Let me see if I can do these calculations, I have been trying to
understand the psychrometric chart, hopefully someone will check me
work.
Assumptions:
• Dryers don't check incoming or outgoing temperature or humidity (they
just pumped heat in and air out) 10 BTU/lb of air
• Air coming in is at 40% relative humidity and 40º; no humidity is
added in house.
• Clothes contain 10 lbs of moisture to be removed.
• Dryer is maximally efficient.
Inside Air:
Dryer gets air at 65º, heats it to 76º increases the humidity ratio by
0.0176 lb of water / lb of dry air.
Drying takes 568 lbs of air, or alternatively 5680 BTUs.
Heating that air takes 5 BTU/lb of air, or 2840 BTUs.
Total = 8520 BTUs.
Outside Air:
Dryer gets air at 40º heats it to 58º, increase the humidity ration by
0.0092 lb of water / lb of dry air.
Drying takes 1086 lbs of dry air, or alternatively 10860 BTUs.
So, from this, using outside air _costs_ you 2350 BTU per load, plus
any leakage in your system.
Thank You Kindly,
Corwyn
--
Corwyn
Kermit didn't know the half of it...
http://www.greenfret.com/
corwyn at greenfret.com
More information about the Greenbuilding