[Greenbuilding] Hydronic Radiant Underfloor Heating
John Straube
jfstraub at civmail.uwaterloo.ca
Sun Oct 14 09:36:53 EDT 2007
Good advice Mr Green, but I would like to add a few details:
The poly should always be directly under the concrete topping otherwise water can and likely will be trapped between the foam and the concrete. This has been a serious problem in many houses. My consulting firm has been involved in investigating problems involving almost 1000 homes because of poly under a sand layer or under foam trapping water. poly on top of the foam directly under the concrete always.
Foil faced insulation only works when facing a gap. It does not matter which way the foil faces as you wont get any benefit. I have done real life field testing of foil under radiant slabs. No radiant exchange benefit if there is not gap.
Chris Green wrote:
> Gary Viljoen wrote:
>> Hi all,
>>
>> I am about to install an under floor hydronic system into the home I am
>> building, and face two options given to me by ‘experts’:
>>
>> 1. Lay the concrete surface bed. Place polystyrene insulation on top.
>> Lay the piping in the screed above this.
>> 2. Insulate below the surface bed with the piping in the concrete
>> surface bed.
>>
>> Any recommendations based on experience?
>>
> Either way, but the first way just adds extra work and probably uses
> more concrete.
>
> My experience recommends this way:
>
> 1: Level and compact the soil/ gravel as best you can. You want to get
> it quite close to flat so there aren't any big voids underneath the
> rigid insulation. Also, getting the bed flat as possible cuts down on
> the amount of concrete you'll need.
> 2: Place 5 1/2"/ 140mm strips of 25 mm rigid insulation along the inside
> of the exterior wall footings or foundation to prevent heat flowing from
> the slab to the foundation and out into the great beyond.
> 3: lay down the poly and seal the joints and any big rips that might
> show up in it. A few little ones are okay. The poly can run up the side
> of the footings a ways. Also tape the poly to any plumbing pipes which
> stick up above the surface. I also use the tape to seal any open pipe
> ends and prevent concrete from splashing into them (that can happen when
> pumping the stuff with a pumper truck...)
> 4: Place the rigid insulation. On one job we even taped the joints
> between the insulation, possibly because we didn't put poly down under
> it...or at least I don't recall doing that...
> ---if you're using foil covered insulation, the foil faces upwards.
> 5: place and tie the rebar as per the specifications. The rebar should
> be between 1 to 1 1/2" or 25 to 40mm above the insulation. There's
> little plastic risers that will set the rebar at the right height but
> chunks of broken concrete patio tiles work just as well.
> 6: lay out and tie the hydronics tubing to the rebar grid.
> 7: do a walkabout to inspect and adjust everything before the cement
> crew starts working. Repair any punctures the rebar has made in the poly...
> 8: pour and screed the concrete.
>
> ***If I think some patches of the compacted soil aren't quite up to my
> standards, I'll ask the rebar guys to throw an extra run or two in,
> reducing the spacing
> from 2' to 1'. I had to do that on one job this spring.
>
>
> Cheers,
>
> Chris Green.
>
>
>
>
> _______________________________________________
> Greenbuilding email list
> Environmentally-preferable design, construction, building elements
> List info: http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.org
> List email: Greenbuilding at listserv.repp.org
> Managed by BuildingGreen, Inc. http://www.buildinggreen.com
> publisher of Environmental Building News and GreenSpec
> Hosted and archived by REPP / CREST http://www.crest.org
> To get on the list:
> http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.org
> or mailto:greenbuilding-request at listserv.repp.org?subject=unsubscribe
> To get off the list:
> http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.org
> or mailto:greenbuilding-request at listserv.repp.org?subject=unsubscribe
>
>
>
>
>
>
--
Dr John Straube, P.Eng.
Associate Professor
Dept of Civil Engineering & School of Architecture
University of Waterloo
Waterloo, ON Canada