Actually, Rob, its the other way around: for roofs, when doing a
non-vented roof assembly, you don't want high vapor permeability: you
want a vapor barrier that keeps any moisture from getting to the "dew
point plane" located somewhere between the inside surface of the ceiling
and the oustide surface of the roof. As long as no moisture/humidity
reaches that plane, then there will be no condensation, and you don't
need ventilation. That's the principle of a non-vented roof assembly.
So for that use, PU foam (or Spray Foam Polyurethane, SFP) functions as
a vapor barrier. I also don't remember the numbers, but I would guess
that beyond an inch or two of closed cell SFP, and maybe less, would
have permeability ratings in the "vapor barrier" range. Of course, we
haven't distinguished between open cell and closed cell foam, which
behave quite differently, in terms of permeability and moisture
absorption. Although the Icynene (open cell) folks will disagree, I
believe closed cell is the preferred foam for non-vented roof
assemblies, as per above.
Warmly, Keith
Vadurro, Rob, EMNRD wrote:
> Regarding vapor permeability and PU foam, I mentioned that PU foam was
> vapor permeable because our local inspectors allow PU roofs to be
> installed over un-vented roof joist space because they consider the PU
> vapor permeable enough to not require the additional joist venting. I
> don't know how this squares with the recent discussion here- perhaps
> we're talking about two different properties that have similar names?
>
> -Rob Vadurro
>
>
>
> Confidentiality Notice: This e-mail, including all attachments is for the sole use of the intended recipient(s) and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited unless specifically provided under the New Mexico Inspection of Public Records Act. If you are not the intended recipient, please contact the sender and destroy all copies of this message. -- This email has been scanned by the Sybari - Antigen Email System.
>
>
>
> _______________________________________________
> Greenbuilding email list
> List info: http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.org
> List email: Greenbuilding at listserv.repp.org
> Managed by BuildingGreen, Inc. http://www.buildinggreen.com
> publisher of Environmental Building News and GreenSpec(r)
> Hosted and archived by REPP / CREST http://www.crest.org
>
>
More information about the Greenbuilding
mailing list