Run a blower door test and prove that the natural ventilation rate exceeds
the ASHRAE specified levels. If called for, damper the fresh air intake,
measure again to ensure that there's still enough.
Make sure you talk to the code official to determine what level of
ventilation is required.
On Feb 19, 2008 8:37 AM, Tom Genovese <tgoyle at yahoo.com> wrote:
> I am auditing a small upstate NY library where they are very sensitive to
> energy costs. They operate 6 hours a day and see intermittent patronage.
> With a new heating system, the installer put 8" ducts to bring in outdoor
> air every time the system runs.
>
> But, the building is 1860s; the warm attic tells me there is plenty of
> air exchange, despite shell upgrades. I want to recommend installing
> dampers in the ducts and closing them as much as they want. Can anyone
> suggest how to make a case for shunning the code-driven fresh air intakes
> that are there?
>
> Thanks,
>
> Tom G.
>
> ---------------------------------
> Be a better friend, newshound, and know-it-all with Yahoo! Mobile. Try it
> now.
> _______________________________________________
> Greenbuilding email list
> Environmentally-preferable design, construction, building elements
> List info:
> http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.org
> List email: Greenbuilding at listserv.repp.org
> Managed by BuildingGreen, Inc. http://www.buildinggreen.com
> publisher of Environmental Building News and GreenSpec
> Hosted and archived by REPP / CREST http://www.crest.org
> To get on the list:
> http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.org
> or mailto:greenbuilding-request at listserv.repp.org?subject=unsubscribe
> To get off the list:
> http://listserv.repp.org/mailman/listinfo/greenbuilding_listserv.repp.org
> or mailto:greenbuilding-request at listserv.repp.org?subject=unsubscribe
>
More information about the Greenbuilding
mailing list