[Strawbale] R value of light straw clay
Rob Tom
ArchiLogic at yahoo.ca
Sun Nov 12 16:20:36 CST 2006
On Sun, 12 Nov 2006 09:56:46 -0500, kim thompson
<shipharbour at ns.sympatico.ca> wrote:
> light straw clay
> Can you tell us where those stats and the later R2-3 that Andrew
> mentions come from.
Kim;
The numbers that I was using to estimate the R-values of Andrew's gable
ends were extrapolated from the chart in Gernot Minke's "Lehmbau-Handbuch"
which is available in an English translation as well.
Minke's book lists straw/clay mixes of densities in the range 300 to 2100
kilograms per cubic metre (18.73 to 131 pounds per cubic foot in Imperial
units) and the corresponding thermal conductivity values of 0.1 to 1.4
watts/metre*degree Kelvin respectively (or 0.60 to 9.71 Btu*in/hr-ft^2 in
Imperial units). The values for thermal resistivity are of course, the
inverse of the values provided for thermal conductivity.
I've provided a chart with conversions of the SIU values to Imperial units
and conversion of the thermal conductivity values to R-values per inch
(way below).
In July 2005, CMHC released a "Research Highlight" entitled:
"Initial Material Characterization of Straw Light Clay" (Technical
Series 05-109)
on a project done by Joshua Thornton. The project officer was of course,
Don Fugler (who else ?).
Thornton reported values of:
Thermal Resistance (per inch): RSI = 0.28 R = 1.6
for a mix of density: 647 kg/m^3 40 pcf
Thermal Conductivity: (for a mix density of) 642 kg/m^3 0.090 W/mK
[Compare Thornton's value for thermal conductivity with Minke's value of
0.17 for a mix of similar density (600 kg/m^3) and whose corresponding
R-value would be R-0.85 per inch, almost half of Thorton's R-value for the
same (almost) density mix.]
Given that the California Energy Commission only allows something like
R-30 for a 3-string bale wall (ie only about R-1.3 per inch, not that I'm
saying the CEC is even remotely accurate)) Thorton's value of R-1.6 for a
straw/clay mix of 40 pcf density seems more than a little optimistic if
not unrealistic.
In any case, I think that the values that Andrew cites, (R-2 to R-3 per
inch for cob are way off and by one decimal place at the very least.
===========================================================
Minke's values converted to Imperial units
Density Conductivity Resistivity
SIU Imperial SIU Imperial Imperial
kg/m^3 lbs/ft^3 W/mC Btu*in/hr-ft^2 R-val per inch
300 18.73 0.1 0.69 1.44
400 25 0.12 0.83 1.20
500 31 0.14 0.97 1.03
600 37 0.17 1.18 0.85
700 44 0.21 1.46 0.69
800 50 0.25 1.73 0.58
900 56 0.3 2.08 0.48
1000 62 0.35 2.43 0.41
1100 69 0.41 2.84 0.35
1200 75 0.47 3.26 0.31
1300 81 0.53 3.68 0.27
1400 87 0.59 4.09 0.24
1500 94 0.65 4.51 0.22
1600 100 0.73 5.06 0.20
1700 106 0.81 5.62 0.18
1800 112 0.91 6.31 0.16
1900 119 1.01 7.00 0.14
2000 125 1.25 8.67 0.12
2100 131 1.4 9.71 0.10
=====================================================
If the above chart gets screwed up by mail programs etc.
there are 5 columns with 19 rows of values
with the values in the first row being
300 (kg/m^3), 18.73 (lbs/ft^3), 0.1 (W/mC), 0.69 (Btu*in/hr-ft^2) and
1.44 (R-value per inch).
That should be enough for you to reconstruct the table if necessary.
Years ago on the CREST SB List, John Cruikshank (aka Sunny John) provided
measured densities for various straw/clay mixes and I quoted and requoted
that post a number of times whenever the topic of R-values of straw/clay
mixes came up. Unfortunately, I can't find Sunny John's post or my
re-quotes at the moment. Perhaps someone else has it on file ?
===* ===
Rob Tom
Kanata, Ontario, Canada
<archilogic at chaffyahoo dot ca>