[Strawbale] Blower Door test set-up
Mark Bigland-Pritchard
mark at lowenergydesign.com
Mon Apr 9 13:23:28 CDT 2007
Derek -
It's a while since I've used one of the things (I used them routinely in
London in the late 80s / early 90s), but I doubt that things have
changed much since then.
Firstly, the seal with the door must be as good as it can possibly be.
Otherwise you get silly results. I got through vast quantities of
masking tape eliminating air gaps between the apparatus and the door
frame on a mix of Georgian, Edwardian and 1960s doorframes, most of
which seemed to suffer from some sort of irregularity....
Secondly, the thing works by measuring static and dynamic pressure
differences between inside and outside at a range of pressures. That
ensures that wind pressure is already taken account of in the readings.
(But it also means that gusting can result in problems in equilibration
and so in unreliable results.) From the data collected, it is possible
to calculate the air flow rate, and hence the air exchange rate, for a
range of pressures. The value for 50Pa pressure difference is found by
interpolation of these results.
If you are not sure of the results, you can always operate the fan in
the other orientation - i.e. do both pressurisation and depressurisation
tests. They should give very similar results to each other.
Now, 50Pa is actually quite a lot more than you would get under normal
circumstances. You don't get to find out what the average "actual" air
exchange rate is by this means - for that you have to apply a fudge
factor which depends on the local windspeeds, possibilities for stack
effect in the building, pressure differences owing to mechanical
movement of air, etc. [Some simple energy assessment packages (like
HOT2000, for example) will decide for you what fudge factor to use and
factor it in when calculating consumption.]
Mark
Derek Roff wrote:
>Shawna said:
>
>
>>If you could find a set of magnahelic gauges, you could possibly make
>> a frame system, but sheesh, to make it airtight is a challenge.
>>
>>
>
>Mark said:
>
>
>>>The blower door method gives you - by extrapolation of results -
>>>a standard figure, usually at 50Pa pressure difference, but relating
>>>that standard figure to what the actual air exchange rate would be
>>>under real conditions is problematic.
>>>
>>>
>
>At a blower-door demonstration, I asked the energy auditor about the
>seal around the door (which didn't look perfect to me) and about the
>wind conditions. He said that the blower door apparatus and
>instrumentation compensated for all that, and other variables, by
>taking direct pressure measurements inside and outside.
>
>At the moment, I can't imagine exactly how that would work. Getting a
>perfect door seal and a windless day would be difficult, but
>compensating for hard to measure variables is also problematic. Were
>these claims a bit of smoke and mirrors? Please tell us more about the
>theoretical and real world issues that affect the accuracy of blower
>door testing.
>
>Derelict
>
>Derek Roff
>Language Learning Center
>Ortega Hall 129, MSC03-2100
>University of New Mexico
>Albuquerque, NM 87131-0001
>505/277-7368, fax 505/277-3885
>Internet: derek at unm.edu
>
>
>_______________________________________________
>Strawbale mailing list
>Strawbale at listserv.repp.org
>http://listserv.repp.org/mailman/listinfo/strawbale_listserv.repp.org
>
>
>
More information about the Strawbale
mailing list