[Strawbale] straw clay insulation values
Rob Tom
ArchiLogic at yahoo.ca
Wed May 2 23:42:22 CDT 2007
On Wed, 02 May 2007 23:37:16 -0400, Daniel Priest <danielpriest at gmail.com>
wrote:
> Anyone have any info on the insulation value of straw-clay?
Daniel;
The following values are from a chart in "Lehmbau-Handbuch" by Gernot
Minke.
If the table gets buggered-up by your email program or the List software,
when reconstructed you should have five columns of values.
In the original chart, there are two columns of values, the first being
for "density" and the second for conductivity, both in SIU (kg per cu
metre and Watts/metre-degree(Celsius) respectively. The conversions for
the corresponding Imperial units and R-value are mine.
(R-value = inverse of conductivity).
Below the chart of values are some empirical observations made by John
Cruikshank (aka Sunny John).
Density Conductivity Resistivity
SIU Imperial SIU Imperial Imperial
kg/m^3 lbs/ft^3 W/mK Btu*in/hr-ft^2 R-val per inch
300 18.73 0.1 0.69 1.44
400 25 0.12 0.83 1.20
500 31 0.14 0.97 1.03
600 37 0.17 1.18 0.85
700 44 0.21 1.46 0.69
800 50 0.25 1.73 0.58
900 56 0.3 2.08 0.48
1000 62 0.35 2.43 0.41
1100 69 0.41 2.84 0.35
1200 75 0.47 3.26 0.31
1300 81 0.53 3.68 0.27
1400 87 0.59 4.09 0.24
1500 94 0.65 4.51 0.22
1600 100 0.73 5.06 0.20
1700 106 0.81 5.62 0.18
1800 112 0.91 6.31 0.16
1900 119 1.01 7.00 0.14
2000 125 1.25 8.67 0.12
2100 131 1.4 9.71 0.10
straw just covered then lightly placed (ie ceiling insulation) 20 pcf
straw coated to point where it is *just* covered then form tamped (normal
wall) 40 pcf
straw just covered, then same amount of additional clay slip added then
form tamped (high mass wall) 70 pcf
--
=== * ===
Rob Tom
Kanata, Ontario, Canada
< A r c h i L o g i c at C h a f f Y a h o o dot C a >
(winnow the chaff from my edress in your reply)